ALLOWABLE LONG TERM DEFLECTION
Muhammad Hashmi
Assalam O Alykum
In one project external consultant IDOM structural engineer is saying that allowable long term deflection ( Flat slab )shall not be checked against the Span length ( center to center)
along the longer length but on the diagonal length ( where the maximum deflection occurs)
 Continuous panel of flat slab 8.3m along horizontal direction and 9.3m along the vertical side and diagonal length is 11.5m.
Which one is correct out of 3 to check the allowable long term deflection. Any reference from code. I am seeing ACI code is silent and unable to provide definition of Ln.
1. 8.3x1000/240 = 35mm
2. 9.3x1000/240 = 38.75mm
3. 11.5x1000/240 = 47mm ( might be multiplied by modification factor calculated for compression steel)
I am also attaching sketch for better understanding
Thank you
QUERY.pdf
Read it again, you will change your your mind.  Read the note 1 of the ACI's table 8.3.1.1 (318-14) meant for the guidance regarding the minimum thickness  for non-prestressed slabs.
Dear Muhammad
Apologies. I approached to one design director of Meinhardt to discuss the issue yesterday. I am hereby attaching his reply along with my query which I had posted yesterday.
What he is saying actually is
 x-direction center to center distance is 8.3x1000/240 = 35mm allowable deflection for column strip in x-direction
 y-direction center to center distance is 9.3x1000/240 = 39mm allowable deflection for column strip in y-direction
for middle panel 12.5x1000/240= 52mm is allowable
Can anybody also give there input
QUERY (1).pdf
I think you are not getting his point. He is saying that if you allow column strip deflection to be 39mm as per L/240 criteria of the code, then that deflection will be translated to a value of 52mm at the mid span of middle strip.
Explanation: For 39mm deflection, the slope of the deflected slab will be 9.3/2/.039 = 119.5 (about 1 in 120); and based on that slope, the midspan deflection will be about 12.46/2/.120 = 51.9mm.
If possible, can you share how are you calculating your long term deflections of two way slab panels?
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik