Water tank leakage
Muhammad Hashmi
Assalam O Alykum
Need supporting ideas to reach conclusions
On one of the construction site attached here photos of water leakage from steel tank RCC Foundations. Tank Capacity is 2,000 M3 and tank is being filled from last 10 days. There was no leakage up to 500-700 M3 water but from yesterday water leakage appears on foundation as water volume is being increased inside tank. Today water volume inside tank is near 1,000 M3 at the current time.
Settlement values after performing the plate load test looks fine around 7mm
and NDT ( Schmidt hammer) the compressive strength of foundation looks also found ok.
Can anybody advise
As a preliminary feedback I advised to check the below with some recommendations
1.       Site team to confirm from the client, any shifting of plumbing is made that is contradicting the original design.
2.       Non utilization of non-shrinkage grouting material at the block out groove which has at least the strength twice the strength of foundations.
3.       Not full fill the supplier recommendations during execution for the connection, might be the cause of leakage and bonding material not used for the jointing of existing and new concrete if any.
4.       Internal cementitious water proofing.
5.       Pressure sealant should be used, furthermore, site team to confirm from the client that, regular maintenance is made for the tank?
6.       Steel tank is wet or dry from outside particularly after 700-meter cube? As leakage is seen after the 700-meter cube volume.
7.       Sand broadcasting can be made to identify the leak spots on the concrete area. Grouting injection might be a solution not sure.
8.     Any leak test is made before utilization of steel tank?
The leak is because of poor welding/ inadequate steel design between the steel base and steel tank walls. I am assuming your tank is not just walls and it has a base. Get a welder to fix it and do seal welds if angles are used on the inside of the base.
You got quiet a few answers above, But i think the fundamental question is what is your tank design is it a steel liner tank with a additional liner layer inside for water proofing or is a pocket base, which i see in this case as the steel wall is embedded in the concrete. There are water seals around the tank wall in the pocket see examples of each below,
that is the liner one
You got that one. There is a waterseal as mentioned above if this seal is not isntalled carefully and if it gets broken or damaged somehow during site pore, the leak at the base can occur.
Normally the concrete slab for such tanks have a very high requirement of crack control so i doubt that if thats not considered in design.
I would recommend first check the design of the wall pocket (if the leak is there) and confirm with the site notes if the seal is provided. The remedial measures can only be suggested once the cause is known. There are several options which can be adopted.
You havenot replied to earlier question of mine, anyways i see this very commonly on the concrete slabs with steel tanks of this size. we do the design and monitoring for such structures on weekly basis. I would recommend you using XYPEX concrete water proofing. This band can be applied outside the tank wall with the concrete. The crystallisation of the compound will stop the water leak. the second option you can use is to empty the tank and apply a band of SikaFlex carbodur sheets at the base of the tank, They will stop that as well.
I haven't seen this design, maybe its more common in "middle east" etc. To me it looks bad, just because if the base is concrete, it will have very tight design requirements on water tightness (as also mentioned above) but also because the underside of foundation in touch with the ground or the sides exposed to sun will result in significant shrinkage demand on the foundation. Might be better to use steel tanks. Just saying.
Its a very common steel tank design for water storage, waste water and fire water in industrial sites all around the world, not used much in Pakistan.
Supplier of steel tank is re-checking the design of steel tank.
On the other hand I communicate with Fosroc guys and they are recommending the below
Dear Mr. Hashmi
 Greetings,
 Regarding to your below inquiry (in case Concrete water tank ) please follow below link for downloading full Technical submittal for following items :
·         Nitofill WS60 :Foaming crack injection resin for stopping water flow
·         Nitofill UR63:Flexible polyurethane injection resin system
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik