Hi everyone,
I have been analyzing a singly story frame slab supported on four beams in SAP and Etabs. However, I am getting greater moments in longer direction than in shorter direction. Please see the attached figures highlighting the local axis as well as moments in both short and longer direction. I am always getting greater moments in longer direction than shorter direction whether I analyze a two-way slab or one-way (I get moments larger moments in longer direction which is not the case I know). Feedback is requested.
Thank you
On 2/23/2022 at 3:48 AM, MSKhan said:
Hi everyone,
Thank you
MS Khan,
I was not  able to gather a complete picutre of the situation from your posted snapshots, but something that comes to mind is that for shells the moment is not about the axis but in the direction of the axis. This is typical nomenclature for all plate analysis softwares.
Please also see this:
Edited by UmarMakhzumi
  • 4 months later...
Hello @ANStructs, @UmarMakhzumi
I came across the same situation as @MSKhanand your reply helped me to figure out what's going on in my design. Thanks.
Most of the resources (books, online forums, videos) I came across on two way slab indicate that moment "will" be higher in the shorter direction than in the longer direction, hence, the reinforcement requirement in the shorter direction becomes higher than the longer direction with the shorter direction reinforcement also placed at a greater effective depth.
But for the exact scenario that @MSKhan indicated above and which I also faced, what if I can't increase the stiffness of the beams in the long direction and I want to keep the beam cross section in the long direction as it is, say due to architectural constraints? Is it a hard and fast rule to "make sure" we have more moment in the short direction? Should I always adjust my beam-to-slab stiffness ratio to make sure that happens? Does it have economic implications? Is it an indicator of excessive deformation of the beams?
Thanks a lot.
“Most of the resources (books, online forums, videos) I came across on two way slab indicate that moment "will" be higher in the shorter direction than in the longer direction..”
In most books, coefficients method for slab design is derived on the assumption that a slab panel is resting on rigid supports i.e. non-deformable supports. Therefore, stiffness of supporting members do not affect the distribution of load from slabs to supporting members. Hence, shorter side of slab which is the more stiffer path carries more load than the longer side.
Whereas in a 3D structural model comprising of beam, column and slab, load is distributed based on relative stiffness of elements connecting at a joint. Stiffer element attracts more load and as in your case, the longer slab span proved to be more stiffer load path than the shorter slab span for load to flow.
“I want to keep the beam cross section in the long direction as it is, say due to architectural constraints? Is it a hard and fast rule to "make sure" we have more moment in the short direction? Should I always adjust my beam-to-slab stiffness ratio to make sure that happens?”
No, you’re not restricted to make sure every shorter direction is the stiffer load path. Assuming the computer model is error free; I would suggest you to properly perform the service and strength design based on the forces you’re getting.
“Does it have economic implications?”
Not that I know of.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik