RCC Walls
Muhammad Hashmi
Assalam O Alykum
In one of our project ( Hospital building) we have Rcc walls are proposing instead of lead shield ( Radiation area for cancer patients).
Rcc walls proposed thickness by the radiation consultant varies from 160mm to 240mm.  Rcc walls are none load bearing, floor to floor height is 4.2m. However, Non-load bearing Rcc
walls height is 3.1m
I want to know is there any code criteria that for such thickness we must have 2 layers of vertical reinforcement and up to that thickness yes we can put 1 layer.
Can you please help in this regard.
For structural walls ACI 318-19 11.7.2.3 states that " For walls with thickness greater than 10 in., except single story basement walls and cantilever retaining walls, distributed reinforcement in each direction shall be placed in at least two layers, one near each face."
However for non load bearing concrete walls you may design your concrete wall as plain concrete walls as per chapter 14 of ACI 318-19.
However if subject wall is not being covered with any sort of sheeting then temperature and shrinkage reinforcement must be provided (equally distributed among both faces), otherwise hair line cracks may appear and can create unrest among users.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik