UBC 97 Response Spectrum Seismic Provisions
Ahmed Waqar
Dear All
If we doing response spectrum analysis as per UBC. do we need to lower our base shear because in UBC it is stated that direct result from spectrum shall be used to design for eerthquakes. If we do so then where is R value.
Dear Mr Umar Makhzumi
Thanks for the feedback!
Artcle # 1631.2 Ground Motion of UBC
It is stated as "The ground motion shall not be reduced by quantity R" so code saying you have to apply full non linear earthquake not being divided by R. Please guide me if i put something wrong.
Yes. When following procedures of UBC Section 1631.2, R value is not to be used
Thanks Mr Uzair.
But if we dont divide it by "R" then base shear becomes almost twice. which is too much. Means we are designing our building ir-respective of the detailing and any structural system as stated in UBC we are giving full earthquake to the structure. Which make no sense to me. Can you please guide me further. If you have any expereince with response spectrum analysis in projects then please share.
Ahmed,
It is explained very clearly  in UBC 97. You need to consider pertinent clauses together. See excerpts below.
1631.5.4 Reduction of Elastic Response Parameters for design.
Elastic Response Parameters may be reduced for purposes
of design in accordance with the following items, with the limitation
that in no case shall the Elastic Response Parameters be reduced
such that the corresponding design base shear is less than
the Elastic Response Base Shear divided by the value of R.
1. For all regular structures where the ground motion representation
complies with Section 1631.2, Item 1, Elastic Response
Parameters may be reduced such that the corresponding design
base shear is not less than 90 percent of the base shear determined
in accordance with Section 1630.2.
2. For all regular structures where the ground motion representation
complies with Section 1631.2, Item 2, Elastic Response
base shear is not less than 80 percent of the base shear determined
3. For all irregular structures, regardless of the ground motion
representation, Elastic Response Parameters may be reduced such
that the corresponding design base shear is not less than 100 percent
of the base shear determined in accordance with Section
1630.2.
The corresponding reduced design seismic forces shall be used
for design in accordance with Section 1612.
Section 1631.5.4 refers to 1630.2, which is your Static Force Procedure. Please see the following topic to understand how to setup your model for Response Spectrum and do the scaling.
You should not reduce it by R if you are performing nonlinear analysis inputting actual R (energy dissipation mechanism). But RSA is a linear method so divide by R (an assumption that building will have ductility in reality so less force).
  • 3 months later...
  • 3 years later...
@jay olleta
Code specify to use I*g/R value as initial scale factor.
But the simple way is to Initially take the scale factor equal to 1000.
Then run the analysis and check/compare the Static and dynamic base shear and update the scale factor accordingly.
If Static Base shear  is greater than Dynamic Base shear, you will need to scale up the dynamic Base Shear
and if Static Base shear is less than Dynamic Base shear, you will need to scale down the dynamic Base Shear as follows:
New Scale Factor=1000*(Static Base Shear/Dynamic Base Shear)
See the UBC code pic attached for the minimum limit of reduction of elastic Response Parameters.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik