Jump to content
  • Welcome to SEFP!

    Welcome!

    Welcome to our community forums, full of great discussions about Structural Engineering. Please register to become a part of our thriving group or login if you are already registered.

Check For Weak Story In ETABS


Areeb
 Share

Recommended Posts

Hello

I would like to check my structure for Vertical irregularity 5a or 5b (according to ACI) i.e check for weak story. It is mentioned that structure has weak story if shear strength of story is less than 80%of shear strength of story above. Also extreme weak story if shear strength of story is less than 65% of shear strength of story above. How to view story strength in ETABS? 

2222.jpg

Link to comment
Share on other sites

Umar,

Yeah I have checked it and by discussing it with other engineers came to find out that ETABS 16  explicitly doesn't provide  data/excel format for identifying the weak story. There is a table for finding out stiffness of each story thereby helping us identify Soft Storey, but Weak Story needs to be done manually.  Software MIDAS provides a table in results clearly displaying Shear Strength of particular storey, but in Etabs it is not present. Yeah by using displacements of adjacent floors it is possible to identify Soft Storey, but that method is not needed now as ETABS clearly gives us Stifnesses of each storey thereby easily helping us to find out Soft Storey in a system. 

Sorry, I have quoted ACI for irregularities its ASCE

Regards,

Areeb Ahmed

 

Edited by Areeb
Link to comment
Share on other sites

To find weak storey, I used to calculate flexure capacity of columns and then divide them with member length to get shear strength of the column. Then I add all the columns shear strength present in one storey to get the shear strength of one storey.

Is this method correct? 

Link to comment
Share on other sites

Hello Fatima,

Well that's a first for me. I think rather than elaborating by calculating flexural capacity and so on you can directly calculate the shear strength capacity of all walls/vertical components in a particular story in particular direction and compare it with the story above thereby finding out whether the system has Vertical Irregularity 5a. or 5b .

Thanks

Link to comment
Share on other sites

  • 3 weeks later...
On 5/20/2018 at 2:26 AM, Areeb said:

Umar,

Yeah I have checked it and by discussing it with other engineers came to find out that ETABS 16  explicitly doesn't provide  data/excel format for identifying the weak story. There is a table for finding out stiffness of each story thereby helping us identify Soft Storey, but Weak Story needs to be done manually.  Software MIDAS provides a table in results clearly displaying Shear Strength of particular storey, but in Etabs it is not present. Yeah by using displacements of adjacent floors it is possible to identify Soft Storey, but that method is not needed now as ETABS clearly gives us Stifnesses of each storey thereby easily helping us to find out Soft Storey in a system. 

Sorry, I have quoted ACI for irregularities its ASCE

Regards,

Areeb Ahmed

 

Can we not used this method of using the storey displacement values given at the very last section of the ETABs summary and divide these values by the storey forces to get the storey stiffness ?? and later compare the stiffness of one storey relative to other above or below it

Link to comment
Share on other sites

On 5/20/2018 at 11:18 AM, Fatima Khalid said:

To find weak storey, I used to calculate flexure capacity of columns and then divide them with member length to get shear strength of the column. Then I add all the columns shear strength present in one storey to get the shear strength of one storey.

Is this method correct? 

This is some thing new to me....You mean Flexural capacity (phi Mn) or the Axial load carrying capacity (Phi Pn) of column divided by length became its shear strength ?? ,,Can i have its reference

Link to comment
Share on other sites

12 hours ago, Zain Saeed said:

Can we not used this method of using the storey displacement values given at the very last section of the ETABs summary and divide these values by the storey forces to get the storey stiffness ?? and later compare the stiffness of one storey relative to other above or below it

Hello Zain

The method which you have mentioned above is for finding out whether the system has soft storey or not. You can use the method mentioned above or ETABS latest version directly gives the stiffness for each storey thereby its easy to find out whether the system has soft storey irregularity.

Link to comment
Share on other sites

  • 2 weeks later...
On 6/11/2018 at 5:05 AM, Areeb said:

Hello Zain

The method which you have mentioned above is for finding out whether the system has soft storey or not. You can use the method mentioned above or ETABS latest version directly gives the stiffness for each storey thereby its easy to find out whether the system has soft storey irregularity.

Thanks .. So for the weak storey, the method mentioned in earlier posts of Mam Fatima  i.e finding flexural strength of column/wall and dividing it by their length is ok ??

Link to comment
Share on other sites

Hello Zain,

The method mentioned by Fathima is new to me. Flexural strength is nowhere related in finding out weak story. As it is clearly defined in ASCE about weak story i.e, the shear strength of story A is less than 80% of shear strength of story B. Shear strength or story strength its same. Then the system is said to contain weak story irregularity

Thanks.

Regards,

Areeb Ahmed.

Link to comment
Share on other sites

For Weak Storey check

If columns are flexure controlled, the shear strength is the shear corresponding to the flexural strength. (Ref: http://www.iitk.ac.in/nicee/IITK-GSDMA/EQ06.pdf)

So I used to calculate flexure strength (Flexural capacity) of column section and then divide this by the length of column to find the maximum shear it can resist before flexure failure may occur. This will give me the shear strength of an individual column. then adding these all will give storey shear strength.

its like adding moment at top and bottom of the column to get the shear force of the column. (the way usually people do to calculate internal forces manually)

I dont have exact reference, but i will research on it and will let you know.

Link to comment
Share on other sites

Hello Fatima,

Well the procedure you have explained is correct for finding out the shear strength of columns, thereby ultimately finding out the story strength. Still I find it cumbersome and we have direct formulas for knowing the shear strength capacity of wall or column thus rather than going by the method of flexural strength we can directly find out shear capacity of wall/column and find out story strength.

Thanks for the update regarding the method used by you. Although cumbersome something new to learn today.😃

Regards,

Areeb Ahmed

Link to comment
Share on other sites

  • 1 month later...

Can we have the formulae as mentioned by Mam Fatima and Mam Areeb. i would really appreciate it. i am making an excel sheet for various seismic checks and the information above would be really helpful.

Thanks

Link to comment
Share on other sites

  • 1 month later...
On 5/20/2018 at 11:18 AM, Fatima Khalid said:

To find weak storey, I used to calculate flexure capacity of columns and then divide them with member length to get shear strength of the column. Then I add all the columns shear strength present in one storey to get the shear strength of one storey.

Is this method correct? 

can't we use story shear graph  (response for lateral forces ) and  apply weak storey check as per code .?

Link to comment
Share on other sites

  • 1 year later...
  • 8 months later...

I just checked the attachment, and it is working. Make sure your are logged in and you can contact admins here.

For ETABS graph of storey shear, is this the applied shear force distribution? I don't use ETABS so you can look up the manual.

 

Link to comment
Share on other sites

  • 1 month later...
On 6/27/2020 at 6:12 AM, Sayed Tanzid said:

Can we use ETABS Graphs of Story Shears to calculate the Story Strenghts? image.thumb.png.824f17a6c99573d7cc399f6af34a922b.png

If story shear is based on applied force then no. Weak story depends on Story Strength which is independent of the force.

 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies