Top and Bottom story range in STATIC LATERAL FORCE PROCEDURE
Fawad
Aoa,
Thank you all the seniors for providing such a nice learning platform.
I am working on the design of a 3 story structure (2 basements+Ground Floor). Base level is at -10m from grade level while top roof (ground top) is +8m from grade level.
Total covered area of building is 100mx60m which is divided into 4 blocks i.e 50mx30m each (See pic attached). Basement retaining wall is provide only at two orthogonal sides (one long and one short side) of each block. But this two sided retaining wall is creating extreme torsion irregularity in my structure. Normal span length is 12m.
So my question is that can i ignore this two sided basement wall in my model ? because this is below grade level and would not contribute in resisting EQ.
Thank you sir @BAZ,
As all my other serviceability checks like drift and deflections are in code allowable limit, so i just amplified/override the eccentricity of my EQX and EQY in load pattern by torsion amplification method as per UBC97 and designed my vertical members accordingly.
Please guide/correct me if i am missing something.
Jazakallah
If you are fine with all other serviceability checks then consider the torsion in your vertical member design.
But keep your eyes on the separation gap between the blocks. The gap must be sufficient enough to avoid pounding action.
You may run real time history (linear model) on your model for deciding the separation gap.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik