Modelling of OverHead Water Tank in Etabs
Dear Engineers!
i need guidance in modelling overhead water tank in etabs. For Top Slab, the spans are 30'x30'. Should i provide beams to support the slab. Further, normally we dont see columns extending to the top and terminates at the verge of shear wall. should i extend the columns beyond the last level and extend it in the water tank walls to support the beams.
Further, if beams are necessary they will cross each other in the middle but will be without any support due to water tank.
lastly, what should be the preferred foundation type. also detailing of RCC wall
Yes, beams are always a good idea as  adding beams would make slab design light and help you manage and design for crack control reinforcement requirements.
Your columns are like boundary elements so you should extend them. Regularity, redundancy & Symmetry should be provided by default for all layouts.
This is okay. However, since your layout is square so important to detail beams rebar as continuous.
Depends on your Geotech Report & Engineer. What is the recommendation by the Geotech? Just check your strength and serviceability limit states (settlement etc) for foundation and go with the one that can meet the demand. Detailing for RCC walls, you can look up either a detailing manual or contact people in the forum if they would like to share go bys with you.
If you are mentioning the water tank walls supported on a frame structure I would preferably address them as retaining walls not as shear walls and detail them as retaining walls. The columns should be extended to the top slab as the water tank walls (retaining walls) will be spanning between them.
Extending the the column through the tank should be done to complete the frame. I have come across some tank designs in which the columns were extended through the tank.
  • 9 months later...
While defining "Mass source" in ETABS for overhead water tanks, do we need to consider complete water load (defined as live in ETABS load pattern) ??? and what are provision in code for its importance factor (1 or 1.25 )
Secondly i have bracing beams (12x18) in rectangular OHWT and i am getting very high top and bottom steel (4.3 inch2) coming in them from ETABS against the load combo 0.9 dead + 1.43) Earthquake (modified load combo as per ACI 350). any idead how to tackle this